Re: Correct generator size

#11579
jatin333
Participant

Puka said:

Supposing I have 3phase power installation, 80A/phase, with 420V/phase as well, what is the calculation for generator to be installed as standby?


generator capacity always in KVA  Your Connected Load  = 1.73*420*80/1000=58KVA Approx.

You have to choose DG Capacity =62.5KVA If your power installation operation in full phase,ok