Reasons For Earthing:There are four basic

reasons for earthing an electrical system:REDUCTION OF SHOCK HAZARDAn

earthed chassis will provide a low impedance path to ground for any

active voltage that appears on the case or metalwork.SAFE DISCONNECTION

OF SUPPLYIf the exposed metalwork of an appliance were connected by a

fault condition to an active conductor, the active current path needs to

be able to flow to ground via a low impedance path so an excessive

current will flow that will cause a protective device such as a fuse or

circuit breaker to open circuit, thus prenting an electric shock

situation.MINIMISE THE DANGER OF FIRE HAZARDThe earth wire should always

be in good contact with all metal parts of any appliance the user may

touch. Should the equipment become faulty by the active wire touching

the case, then current will rush to earth, smoke will rise from the

equipment, and if the current is very high the fuse in the active line

will blow, disconnecting mains power from the faulty appliance. Without

the earth wire, this fault would go undetected, allowing high current to

flow through the patient whenever the patient formed a circuit to

ground. Standards limiting current in any circuit are vital to prevent

excessive heating of the power supply wires leading to fires.VOLTAGE

STABILITYNeutral earthing : Star point of Wye connected transformers and

alternator windings are earthed primarily to provide voltage stability

to system on account of imbalance in loading resulting in neutral

current flow. Neutral point allows vector sum of three phase currents

displaced at 120 degrees nullifying it to zero. Secondary purpose served

is detection of earth faults or earth leakages and allow the protective

gear to operate in desired time.In the view of high harmonic contents

found in modern facilities, the zero sequence or triplen harmonic

currents overload the neutrals if not adequately sized. This is because

these are in phase and hence do not cancel out at neutral point. So

neutrals are required to be sized equal to or sometimes double the size

of line conductors to carry “algebraic sum” of triplen components in the

lines. Neutral earthing for applicable to low voltage distribution

systems upto 1000 V ac comprise of solid earthing with no intentional

resistance connected in the path. Visit following