Home › Electrical Engineering Forum › General Discussion › Applications where LV fuses are technically more adapted than LV circuit-breakers? › Re: Applications where LV fuses are technically more adapted than LV circuit-breakers?
2012/03/05 at 3:42 pm
#12865
olivier bouilliez
Participant
Agree with holwa on discrimination for small ratings . Be careful to at least have a gap in the fuse ratings series . For example, you may loose discrimination with 10A, 16A, 25A . In this case, the three ratings are too close.