the best ever voltage drop calculation spreadsheet
2012/01/07
6:04 pm
elec master
Member
Forum Posts: 16
Member Since:
2011/12/29
Offline

This voltage drop calculator will provide an approximate value for use in project design and it is based on the following public domain formula.

NEC Rules controlling Voltage Drop:

NEC article 210.19(A)(1) FPN No.4 and 215.2(A)(3) FPN No.2 :

These FPN’s (Fine Print Notes) suggest that a design with no more than 3% voltage drop for feeders and no more than a total of 5% voltage drop in branch circuits to the farthest outlet will provide reasonable efficiency at operation.

Note: Even though FPN’s (Fine Print Notes) in this case are not code requirements but recommendations, it is still good engineering practice to closely follow these guidelines

NEC article 647.4(D):
For Sensitive Electronic Equipment, The voltage drop on any branch circuit shall not exceed 1.5 percent and the combined voltage drop feeder and branch-circuit conductors shall not exceed 2.5 percent.

NEC article 647.4(D) (1):
For Fixed Equipments, The voltage drop on branch circuits supplying equipment connected using wiring methods in Chapter 3 shall not exceed 1.5 percent and the combined voltage drop of feeder and branch-circuit conductors shall not exceed 2.5 percent.

NEC article 647.4(D) (2):
For cord-connected equipment, The voltage drop on branch circuits supplying receptacles shall not exceed 1.0 %. For the purposes of making this calculation, the load connected to the receptacle outlet shall be considered to be 50 percent of the branch-circuit rating. The combined voltage drop of feeder and branch-circuit conductors shall not exceed 2.0 %.

NEC Article 695.7:
For Fire pumps, the voltage at the controller line terminals shall not drop more than 15 percent below normal (controller-rated voltage) under motor starting conditions. The voltage at the motor terminals shall not drop more than 5 percent below the voltage rating of the motor when the motor is operating at 115 percent of the full-load current rating of the motor.

Exception: This limitation shall not apply for emergency run mechanical starting.[NFPA 20, 6.4]

This spreadsheet includes three different worksheets as follows:

1-Voltage Drop Calculator worksheet
2-Summary worksheet
3-Information worksheet

to read more and download your copy , please follow the link:

http://alihassanelashmawy.blog…..tions.html

Forum Timezone: UTC 1

Most Users Ever Online: 93

Currently Online:
20 Guest(s)

Currently Browsing this Page:
1 Guest(s)

Top Posters:

Spir Georges GHALI: 150

electricalexpert65: 33

Chris2011: 32

jatin333: 28

Ally Kanyondo: 28

Francois: 22

Member Stats:

Guest Posters: 784

Members: 11797

Moderators: 4

Admins: 1

Forum Stats:

Groups: 1

Forums: 2

Topics: 645

Posts: 2299

Newest Members: soha, ekrem.kolu, kc_5110, tonmoy, rajesh choudhary, mithlesh pandit

Moderators: Laurent (54), Sudeep (18), Nawaz (12), erickench (38)

Administrators: admin (18)

Electrical engineering Community is proudly powered by WordPress
Entries (RSS) and Comments (RSS) and license Creative Commons License

webleads-tracker