Power factor correction kvar policy in countries
Read the original blog post
2010/10/19
9:00 am
Francois
Member
Forum Posts: 22
Member Since:
2009/03/02
Offline

I want to share with you information about regulations and policies in different countries about power factor correction: are penalty levels specified, which levels ?

Most of people know the main benefits of power factor correction
  • Increase the power availability or reduce the size of the electrical installation,
  • reduce losses and as a consequence contribute to the reduction of CO2 emissions,
  • make saving on energy bill when penalties are applied.

From my point of view, charge the reactive power in the electricity billing is the best way to push power factor correction, because it gives a fast return on investment.
I found information regarding the reactive power billing policy in some 16 countries:
Germany, Austria, Canada, Spain, France, Portugal, Baltics, Roumania, Russia, UK, USA, Thailand, China, Australia

you can have a look to this xls file and you can complete it  for the countries you know by writing a Comment below … and i will then come back with an updated table

And I'm really surprised how huge is the difference between the countries and between the utilities in some countries.

Working at Schneider-Electric, i can also advise you to use the technical information given in the Electrical Installation Guide, chapter L : a good overview about power quality & power factor correction
example of topics covered :

  • Why to improve the power factor?
  • How to improve the power factor?
  • How to decide the optimum level of compensation?
  • Example of an installation before and after power factor correction

Jacques Peronnet

2010/10/19
9:01 am
endar
Guest

it is nice information about PF. thanks

2010/10/19
9:01 am
pranav
Guest

In countries like India, where there are no charges for reactive power at consumer level, I think utilities should install those meters than can measure reactive power also. Only then consumers will try to improve the power factor of their loads.

2010/10/19
9:01 am
David Berger
Guest

In ISRAEL there is a penalty for under 0.92 for low voltage consumers and under 0.90 for hi-voltage consumers. It is checked monthly and the penalty is 0.1% (of the electric bill) for every 0.001 deviation.

2010/10/19
9:01 am
Heinz R.
Guest

I am an Electrical Engineer in the USA and I don't understand your Comments.

1) Electrical rates in the USA do not vary by State, they vary by a) Power company, b) and the type of consumer – for example, residential, industrial or commercial, and even within these there are several types of rates. One power company may supply power to several States or there may be several power companies in one State. Furthermore, rates often vary by the amount of power consumed, the time of day and often the season. Only very rarely are poor power factor penalties charged to residential users. Lastly, electric rates are not set by the States but by the power companies under the oversight and approval of the responsible Public Service Commission.

2) What do you mean with your $3 per KVAR comment? Actually, the most common way that power companies impose the power factor penalty is by charging for KVA-HRs used rather than KW-Hrs.

2010/10/19
9:01 am
andery
Guest

Why do You think that Russia don't have a penalty? They have. I live in Ukraine and we also have a penalty. I don't know what is the price of reactiv power in our country, but now almost every new building with power over 50kWatt has а reactive power compensation. cos phi have to be near 0.95.

Sorry for my bad english.

2010/10/19
9:01 am
Johnya
Guest

I didn't understand the concluding part of your article, could you please explain it more?

2010/10/19
9:01 am
Juan
Guest

in Mexico there is a penalty if you are under 90% of power factor, but also there olso a bonus if you are above only for industrial loads, they use this 2 formulas: total_energy_bill_PF_carge_%= (3/5)*((90/PF)-1)*100, total_energy_bill_PF_bonous_%= (1/4)*(1-(90/PF))*100

2010/11/14
3:05 am
bvcshekar
Member
Forum Posts: 3
Member Since:
2010/11/14
Offline

power factor improvement is done to reduce losses upstream. What if the compensating equipment consumes many times more energy than it saves upstream? Are there standards fixing the wattloss/kvar of compensating equipment?

2010/11/19
9:12 am
rockz04
Guest

in our country philippines, most of our power factors here is in 0.86 only..

2010/11/24
8:43 pm
andre_cirilo1
New Member
Forum Posts: 1
Member Since:
2010/11/24
Offline

Great information!

I am Electrical Engineer and will inform soon as occurs in Brazil demand reactive

2010/12/04
6:58 am
Shafiq Ahmed
Guest

this information is very informative for all electrical engineer and electric lover, thank you for sharing.


2010/12/13
2:42 pm
Yasin
Guest

in our country, the cos phi level is 0.98 so its almost impossible to compensation with only using 3-p capacitors, you should use also 1-p capacitors. as you may know, electric energy is getting expensive year an year and most of utulities are going to level up cos phi level their countries. so why? because reactive energy is waste as for us.
also this information is very good, thanks a lot.

2010/12/13
2:43 pm
Yasin
Guest

by the way, my country is Turkey :)

2010/12/24
5:33 am
liew_mic
New Member
Forum Posts: 2
Member Since:
2010/12/23
Offline

I am mic from singapore.

our Power factor (cosQ) 0.85, if below than that, owner have to responsible for the electical bill.because our electrical from 22kv/6.6kv is purchase from company instead of government. in many matter to increase the power factor equal to 1.

2010/12/27
7:33 am
Rizwan
Guest

Yasin said:

by the way, my country is Turkey :)

Now a days in India, in Mumbai distribution APFC's are used to maintain P.F , in RSS depending upon the requirement capacitor banks are installed to improve the pf at transmission level. But due to some industries the power factor reduces which increases line current and some drop in voltage, depending upon the requirement they are charged and discharged. HT consumer's are penalized for the p.f if it goes below 0.98 and a compensation is given if thy maintain p.f more than 0.99.


2011/01/11
6:33 am
sinnadurai sripadmanaban
Member
Forum Posts: 3
Member Since:
2010/07/21
Offline

1)Should we disconnect capacitor bank when powered by a generator?.

2)Can somebody give ratings of capacitors for starting(reducing starting current) induction motors for various sizes of motors(hp/rpm)?.

3)Can somebody give ratings of capacitors for pfc of individual motors of different hp/rpm

Thanks

2011/01/13
5:24 pm
Juan Carlos
Guest

By the rules in Brazil, users supplied at voltages greater that 2.3 kV (group A) must have their PF verified by the utility in a mandatory and permanent way (art. 34, reg. 456/00). Users supplied at voltage lower than 2,3 kV (group B) can measure their PF in a facultative way. If that PF is lower than 0.92 (inductive or capacitive), reactive energy consumption and demand are mesure and charges apply (Art. 49, reg. 456/00). Furthermore, according to art. 68, reg. 456, users from group B can be charged by their reactive energy and demand, if their PF is lower than 0,92 during a minimum period of 7 days. From my point of view, if utilities adopt electronic meters to also register the PF of residential users, there are no regulation that don't allow them to charge us by the reactive energy. So, the end is near… Are you agree?

2011/01/15
12:31 pm
Sylvester
Guest

Can any one on the list inform me correct connection of Power factor capasitors to be installed after the Electricity meter or else on the bus bar.

 

Sylvester.

2011/01/15
3:20 pm
Sylvi
New Member
Forum Posts: 1
Member Since:
2011/01/15
Offline

In Srilanka no penaly or any surcharge for power Lag.

Sylvester.

Forum Timezone: UTC 1

Most Users Ever Online: 93

Currently Online:
22 Guest(s)

Currently Browsing this Page:
1 Guest(s)

Top Posters:

Spir Georges GHALI: 150

electricalexpert65: 33

Chris2011: 32

jatin333: 28

Ally Kanyondo: 28

Francois: 22

Member Stats:

Guest Posters: 784

Members: 11797

Moderators: 4

Admins: 1

Forum Stats:

Groups: 1

Forums: 2

Topics: 645

Posts: 2299

Newest Members: soha, ekrem.kolu, kc_5110, tonmoy, rajesh choudhary, mithlesh pandit

Moderators: Laurent (54), Sudeep (18), Nawaz (12), erickench (38)

Administrators: admin (18)

Electrical engineering Community is proudly powered by WordPress
Entries (RSS) and Comments (RSS) and license Creative Commons License

webleads-tracker