Home › Electrical Engineering Forum › General Discussion › CALCULATION OF KVA RATING OF WELDING T/F WITHOUT NAME PLATE
- This topic has 4 replies, 3 voices, and was last updated 15 years ago by
admin.
- AuthorPosts
- 2011/06/16 at 4:16 pm #10518
admin
KeymasterDEAR ENGINEERS
CAN YOU GIVE ME A SUITABLE WAY TO CALCULATE THE KVA RATING OF A WELDING MACHINE HAVING NO NAME PLATE
ALSO HOW CAN WE UNDERSTAND THE CAPACITOR CONNECTED IN COMBINATION WITH A POWER EQUIPEMENT IS PROPERLY WORKING?
2011/06/29 at 5:24 pm #12235Sunny Boy
ParticipantHi
If there is a transformer in your welding machine you may calculate transformers power. I found one very approximate equation for calculating real power of a transformer.
P=A*A, where A is cross section of transformers core.
I usually test capacitors with current clamps. I use Fluke 345 which can actually measure the amount of active and reactive power consumed by a capacitor. You can compare measured data with data on capacitors nameplate.
If you have ordinary clamp meter you may assume that all current is reactive. With use of reactive current, voltage and nominal capacity you can calculate actual reactive power of capacitor. But note that capacitors power is proportional to voltage squared (U*U).
I hope that this information is useful.
Best regards,
Miha
2011/06/29 at 8:08 pm #12237admin
KeymasterSunny Boy said:
Hi
If there is a transformer in your welding machine you may calculate transformers power. I found one very approximate equation for calculating real power of a transformer.
P=A*A, where A is cross section of transformers core.
I usually test capacitors with current clamps. I use Fluke 345 which can actually measure the amount of active and reactive power consumed by a capacitor. You can compare measured data with data on capacitors nameplate.
If you have ordinary clamp meter you may assume that all current is reactive. With use of reactive current, voltage and nominal capacity you can calculate actual reactive power of capacitor. But note that capacitors power is proportional to voltage squared (U*U).
I hope that this information is useful.
Best regards,
Miha
G S DAS said:
DEAR ENGINEERS
CAN YOU GIVE ME A SUITABLE WAY TO CALCULATE THE KVA RATING OF A WELDING MACHINE HAVING NO NAME PLATE
ALSO HOW CAN WE UNDERSTAND THE CAPACITOR CONNECTED IN COMBINATION WITH A POWER EQUIPEMENT IS PROPERLY WORKING?
Measure the current and voltage.
kVA = volts x amps. 1-phase
kVA = 1.732 x volts x amps – 3-phase
2011/06/30 at 7:26 am #12241ramzy2006
ParticipantDear
For the above mentioned, the situation depend on if you have electric measuring instrument or not, if yes what you have then you can decide
In a present of jus clamp meter you can measure the current and volt
KVA =V*I
If you have just multi-meter reading ohm and volt
You can calculate the resistance of the welding machine direct=R
Then
KVA = V2/R
2011/10/08 at 1:53 pm #12547admin
KeymasterWelding Machine commonly rated in amperes. And most of welding machine have 50V secondary winding or use a volt meter to measure it exactly. To calculate the kVA=(ampere rating x secondary voltage) / 1000.
- AuthorPosts
- You must be logged in to reply to this topic.