ABB lv sace switchgear

Home Electrical Engineering Forum General Discussion ABB lv sace switchgear

Viewing 3 posts - 1 through 3 (of 3 total)
  • Author
    Posts
  • #10377
    admin
    Keymaster

    hi anybody ever had problems with the spring mechanisms on SACE E2N 12

    #11851
    admin
    Keymaster

    Yes, several times. These breakers need to be used at least once per year or they need to be dismantled & cleaned & lubricated. In particular the pawls on the manual charging mechanism stick.

    #11855
    admin
    Keymaster

    Yes – problems with CB being closed when it indicates open.  Current solution is to fit long allen bolts to ensure cb can be used as a point of isolation

Viewing 3 posts - 1 through 3 (of 3 total)